What is the temperature coefficient (alpha) typically used for Pt100 RTDs?

Prepare for the IandE Technician Test. Use flashcards and multiple-choice questions to reinforce knowledge. Each question includes hints and explanations to aid your understanding. Ace your exam with confidence!

Multiple Choice

What is the temperature coefficient (alpha) typically used for Pt100 RTDs?

Explanation:
Alpha is the fractional change in resistance per degree of temperature. For platinum resistance thermometers like the Pt100, the standard value used is about 0.00385 per degree Celsius. This means every 1 °C rise increases the resistance by roughly 0.385% of its value at 0 °C. For a Pt100 (100 Ω at 0 °C), a 1 °C increase adds about 0.385 Ω, giving around 100.385 Ω; at 100 °C, the resistance is about 138.5 Ω if you use the linear approximation. The other options don’t fit because they imply either too large or too small a change per degree, or they use a per-degree-Fahrenheit unit, which isn’t the standard for Pt100 RTDs.

Alpha is the fractional change in resistance per degree of temperature. For platinum resistance thermometers like the Pt100, the standard value used is about 0.00385 per degree Celsius. This means every 1 °C rise increases the resistance by roughly 0.385% of its value at 0 °C. For a Pt100 (100 Ω at 0 °C), a 1 °C increase adds about 0.385 Ω, giving around 100.385 Ω; at 100 °C, the resistance is about 138.5 Ω if you use the linear approximation. The other options don’t fit because they imply either too large or too small a change per degree, or they use a per-degree-Fahrenheit unit, which isn’t the standard for Pt100 RTDs.